ReOPT not happy with negative numbers #160
Unanswered
hmurphy02
asked this question in
1 - General REopt Questions
Replies: 1 comment
-
Hi, REopt currently does not accept negative load values. If these negative values are because there is existing PV, you might consider backing out the PV generation, creating a "gross load" (rather than net load) profile, and using the "existing PV" input to indicate that there is existing PV. If you enter the gross load + existing PV, be sure to set |
Beta Was this translation helpful? Give feedback.
0 replies
# for free
to join this conversation on GitHub.
Already have an account?
# to comment
-
Hi all,
I've been working with reopt to help with a school, we were given all the data we need, but a lot of it is negative numbers. After trying to plug in the negative numbers to reopt, it wont seem to run, but when i take them out, it runs. the negative numbers are essential in getting a correct size system for the school. Anyone help?
Beta Was this translation helpful? Give feedback.